Does my panel support an EV charger and a dryer at the same time?

Updated 2026-11-11. Educational page, not a permit calculation.

It depends on the service size and on whether the two loads can run at once. A 32-amp charger is a continuous 7.68 kW load at 240 V; an electric dryer is also a large 240-volt load. On many 200-amp services the pairing fits a load calculation; on many 100-amp services it does not, or it fits only with a lower charger setting or load management.

This is the coincident-use version of the EV-plus-dryer question. If you charge in the evening while laundry runs, the electrician should not treat the dryer as something that never overlaps the charger.

Same 5,400 VA dryer example and 32 A EVSE, now compared with a 100 A service.
Step (2023-style optional method, educational)Result
General lighting at 3 VA/ft²5,400 VA
Small-appliance and laundry circuits at 1,500 VA each4,500 VA
General load including listed nameplates and EVSE22,980 VA
First 10 kVA at 100%, remainder at 40%15,192 VA
Larger of the heating or cooling values entered, at 100%4,000 VA
Calculated load19,192 VA · 80.0 A at 240 V
Compared with this walk-through’s service rating80.0 A is under a 100 A rating by 20.0 A

Educational walk-through of the optional dwelling-unit method structure in NEC 2023 220.82. Not a permit calculation. 220.82(C) heating/cooling selections can be more involved than “the larger of two numbers,” especially with heat-pump backup strips.

On a 100 A service this walk-through is about 80.0 A — tight enough that a 40 A or 48 A charger, or an electric range on top, can change the answer. The 200-amp version of this pairing is on the dedicated 200-amp page. A listed load-management device can pause the charger while the dryer runs, which is a different solution from a heavy-up. Use the calculator.

This is not a permit calculation, a utility approval, or a substitute for a licensed electrician, HVAC contractor, or the authority having jurisdiction. Panel Headroom is an independent educational site. It is not a utility, a certification body, or a contractor. Electrical and generator work that is done incorrectly can cause fire, shock, or carbon monoxide poisoning. Use the adopted electrical code and manufacturer instructions; pull permits where required.