Heat pumps

Heat pump vs furnace operating cost in Illinois or Ohio

Updated 2026-11-11. Educational page, not a permit calculation.

Not at the state averages, using these ratings. Illinois: 17.67¢/kWh and $11.25/Mcf (1,048 Btu/cf) → about 11.30/MMBtu for a 95% furnace vs 21.81 for an 8.1 HSPF2 heat pump. Ohio: 16.90¢/kWh and $13.85/Mcf (1,062 Btu/cf) → about 13.73 vs 20.86. Both comparisons favor the furnace on unit cost. Illinois’s cheap residential gas is especially hard for the heat pump to beat at these ratings; Ohio is a bit closer and still favors gas.

Illinois and Ohio versus the U.S. average.
StateResidential electricity, 2025 (¢/kWh)Residential gas ($/Mcf)Implied $/therm95% AFUE furnace ($/MMBtu)8.1 HSPF2 heat pump ($/MMBtu)
Illinois17.6711.25 (2025)1.0711.3021.81
Ohio16.9013.85 (2025)1.3013.7320.86
United States17.2315.34 (2025)1.4815.5921.27

Electricity from EIA Electric Power Annual Table 2.10, 2025 residential, final, retrieved 2026-11-11. Gas and heat content from EIA annual series, release 2026-10-30. Therms per Mcf = heat content (Btu/cf) / 100. Furnace cost = (gas $ per therm × 10) / 0.95. Heat-pump cost = (1,000 / 8.1) × electricity $/kWh. HSPF2 8.1 is ENERGY STAR’s cold-climate minimum for ducted / packaged units, used here as a labeled rating, not a prediction of your climate. State averages are not your tariff.

This is the climate of the Chicago-suburbs dual-fuel threads: winters colder than DOE Region IV, and gas that is often cheaper per unit of delivered heat than electricity at an 8.1 HSPF2. A full-electric cold-climate heat pump can still be the right comfort and decarbonization choice; it is not automatically the cheaper operating-cost choice at these averages. Dual fuel, or a commissioned changeover, is how many owners stop arguing with January. Use the calculator with your rates, and see the dual-fuel and backup-furnace pages.

This is not a permit calculation, a utility approval, or a substitute for a licensed electrician, HVAC contractor, or the authority having jurisdiction. Panel Headroom is an independent educational site. It is not a utility, a certification body, or a contractor. Electrical and generator work that is done incorrectly can cause fire, shock, or carbon monoxide poisoning. Use the adopted electrical code and manufacturer instructions; pull permits where required.